Here is a good one to think about.
Overhead service 120/240 to a single gang meter base. From the meter base there are two main panels. One "A" is located in the basement and the other "B" is located on the other side of the house. Immediately inside the basement where the SE comes through the wall is Panel "A" and right along side it is the disconnect for Panel "B".
There is a #4 Cu GEC coming from a CEE that ties directly to the Disco for Panel "B". From there it jumps over to Panel "A" to provide the GEC. There are 2 separate lugs on the neutral bar of the disco.
Panel "A" provides the 1/0 Cu bond to the water pipe.
Is this a legal install under the 2005 NEC?
Here is the story in pictures:
Panel B disco on left, Panel A on right
Inside the disco to Panel B where the GEC feeds over to Panel A
Inside Panel A which is the only point that the H20 bond comes from
Subfed Panel B that has issues with the equipment grounding bars
Overhead service 120/240 to a single gang meter base. From the meter base there are two main panels. One "A" is located in the basement and the other "B" is located on the other side of the house. Immediately inside the basement where the SE comes through the wall is Panel "A" and right along side it is the disconnect for Panel "B".
There is a #4 Cu GEC coming from a CEE that ties directly to the Disco for Panel "B". From there it jumps over to Panel "A" to provide the GEC. There are 2 separate lugs on the neutral bar of the disco.
Panel "A" provides the 1/0 Cu bond to the water pipe.
Is this a legal install under the 2005 NEC?