Ok, not my forte` (heck I'm just getting the lingo down), but I am seeing installations approved that don't appear correct.
I'm going to lay out how I interpret the code, and I'd appreciate if you guys could steer me in the right direction.
IRC states that the GEC and the bonding jumpers must be sized in accordance with E3503.1.
In examining E3503.1 for a 2/0 200a service (2/0 being the governing factor in the table, not the amperage), I see that the minimum conductor size is 4ga copper.
What I am used to seeing is (2) grounding rods installed 6' apart. Each rod has a #6 conductor to the panelboard. I see that E3503.1 fn d says, in part, "Where the sole grounding electrode system is a ground rod or pipe as covered in Section E3508.2, the grounding electrode conductor shall not be required to be larger than 6 AWG copper or 4 AWG aluminum."
So I get where the #6 is coming from. Rather than do the resistance test, they pound a second rod per E3508.4.
What I don't get is why #6 is allowed when a metal underground water pipe is bonded (maybe it shouldn't be). The same is true of a system that may have an CEE and a ground rod. In these scenarios shouldn't the GEC and bonding jumper be a #4?
I have never seen an install without the ground rods. Am I missing something, or could you simply bond an underground water pipe with a #4 and forgo the ground rods altogether? The same question with a CEE?
Sorry if these seem like trivial questions; what I think I know and what I see are two completely different things. I'm not too ashamed to ask for help!
Thanks!
I'm going to lay out how I interpret the code, and I'd appreciate if you guys could steer me in the right direction.
IRC states that the GEC and the bonding jumpers must be sized in accordance with E3503.1.
In examining E3503.1 for a 2/0 200a service (2/0 being the governing factor in the table, not the amperage), I see that the minimum conductor size is 4ga copper.
What I am used to seeing is (2) grounding rods installed 6' apart. Each rod has a #6 conductor to the panelboard. I see that E3503.1 fn d says, in part, "Where the sole grounding electrode system is a ground rod or pipe as covered in Section E3508.2, the grounding electrode conductor shall not be required to be larger than 6 AWG copper or 4 AWG aluminum."
So I get where the #6 is coming from. Rather than do the resistance test, they pound a second rod per E3508.4.
What I don't get is why #6 is allowed when a metal underground water pipe is bonded (maybe it shouldn't be). The same is true of a system that may have an CEE and a ground rod. In these scenarios shouldn't the GEC and bonding jumper be a #4?
I have never seen an install without the ground rods. Am I missing something, or could you simply bond an underground water pipe with a #4 and forgo the ground rods altogether? The same question with a CEE?
Sorry if these seem like trivial questions; what I think I know and what I see are two completely different things. I'm not too ashamed to ask for help!
Thanks!