• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

GFCI Protection Requirements NEC 210.8(D) in the 2023 NFPA 70

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,051
Location
Somewhere Too Hot & Humid
Some big changes for 120/208/240 vac appliances:


210.8
(D) Specific Appliances.
GFCI protection shall be provided for the branch circuit or outlet supplying the following appliances rated 150 volts or less to ground and 60 amperes or less, single- or 3-phase:
  • (1) Automotive vacuum machines
  • (2) Drinking water coolers and bottle fill stations
  • (3) High-pressure spray washing machines
  • (4) Tire inflation machines
  • (5) Vending machines
  • (6) Sump pumps
  • (7) Dishwashers
  • (8) Electric ranges
  • (9) Wall-mounted ovens
  • (10) Counter-mounted cooking units
  • (11) Clothes dryers
  • (12) Microwave ovens
But that's not all. You still have to look at 422.5(A) & (B) for appliances.
422.5
(A) General.
Appliances identified in 422.5(A)(1) through (A)(7) 150 volts or less to ground and 60 amperes or less, single- or 3-phase, shall be provided with Class A protection for personnel. Multiple Class A protective devices shall be permitted but shall not be required.
  • (1) Automotive vacuum machines
  • (2) Drinking water coolers and bottle fill stations
  • (3) Cord-and-plug-connected high-pressure spray washing machines
  • (4) Tire inflation machines
  • (5) Vending machines
  • (6) Sump pumps
  • (7) Dishwashers

(B) Type and Location.
The GFCI shall be readily accessible, listed, and located in one or more of the following locations:
  • (1) Within the branch-circuit overcurrent device
  • (2) A device or outlet within the supply circuit
  • (3) An integral part of the attachment plug
  • (4) Within the supply cord not more than 300 mm (12 in.) from the attachment plug
  • (5) Factory installed within the appliance
 