I-2 hospital built under 1970's UBC Type I construction, fully sprinkled and this floor has been updated to quick response sprinkler heads. UBC required corridors serving an OL of over 30 to be rated one-hour. There is an existing coffee bar that also sells bottle drinks, sandwiches, soups, prepackage salads all prepared in the main hospital kitchen. They would like to remove the one-hour rated wall and have the area open to the corridor. 407.2 has an exception that would allow less than 500 sq ft for a "Gift Shop" This area is about 400 sq ft and the Architect would like to say this is a similar use as a "Gift Shop". The hospital also has to comply with NFPA Life Safety 101 if it is more restrictive and I have no idea what it may or may not allow.
Please all thoughts and opinions or code language that will aid in documenting the final decision if this can be permitted or not will be very helpful
407.2.4 Gift shops.
Gift shops and associated storage that are less than 500 square feet (455 m2) in area shall be permitted to be open to the corridor where such spaces are constructed as required for corridors.

Please all thoughts and opinions or code language that will aid in documenting the final decision if this can be permitted or not will be very helpful
407.2.4 Gift shops.
Gift shops and associated storage that are less than 500 square feet (455 m2) in area shall be permitted to be open to the corridor where such spaces are constructed as required for corridors.