• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Glazing in Fire Wall

jl3

Registered User
Joined
Jun 4, 2020
Messages
14
Location
Denver, CO
We have storefront within a fire wall and as I understand it, fire-resistance-rated glazing assemblies can be utilized within a fire wall. That being said, can we use normal glazing and provide a vertical/side acting fire shutter instead, or does the glazing need to be rated regardless?
 
Yes, provided that the opening complies with Section 706.8 (2018 IBC). If either building is not sprinklered, then the opening area is limited to 156 sq. ft. Whether sprinklered or not, the aggregate width of all openings on a story cannot exceed 25% of the fire wall's overall length.
 
  • Like
Reactions: jl3
We have storefront within a fire wall and as I understand it, fire-resistance-rated glazing assemblies can be utilized within a fire wall. That being said, can we use normal glazing and provide a vertical/side acting fire shutter instead, or does the glazing need to be rated regardless?


Why is there a firewall??
 