• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Glazing near a sidewalk a the dealership

SCBO1

Platinum Member
Joined
Oct 28, 2009
Messages
4,367
Location
MID WEST
Dealership shows 1" insulated glass (not tempered) in the exterior wall glass panels over 9sf and a 2" wide seperation mullion between the bottom sections of glass.

My question is, would the seperation mullion be considered the protective bar if between 34"-38".

IBC2006 section 2406.3 7. exception. Would this exception apply to prevent the glass from being tempered safty glass?

pc1
 
The use of a mullion between 18 and 36 inches above the floor is the typical way of avoiding this requirement. see conditions 7.2 and 7.3
 