We have a new steak house going into an old building. The grease duct has been routed through the building, penetrates an exterior wall at the top of first floor, goes up the side of the building to the third floor where it the goes back onto the roof and exhausts. The contractor terminated the duct enclosure (wrap) where it exits the building at the first floor. At final my inspectors call the contractor on it, citing 2012 IMC 506.3.11.2, which states the enclosure must be continous to the outlet terminal. The engineer is claiming the outlet terminal is where the duct exits the building, not the exhaust outlet. I know they need to protect it as required by 506.2, and part of me has trouble with requiring the wrap on the exterior of the building, but I think the outlet terminal is the point of exhaust. Opinions?