Serious quagmire alert, but I will start simple.
Stipulate that a greenhouse is a group U per 312.1.

2018 IBC t506.2, footnote i says "or the allowable area area shall be permitted to comply with table C102.1 of appendix C". That table increases the allowable area. Generally, the appendices are only used if adopted, but since the code directs us there does that change anything? Now, to add on...when I read appendix C in it's entirety, I notice that per C102.2, a greenhouse can be unlimited in area with 60' yards. But that is not tC102.1 as referenced in the footnote.

This AHJ has not adopted appx. C. So if I can use only t102.1 via the direct code reference I can use those values. But, I don't think I get to use anything else in the appendix, which is the real issue based on the size of the building.

Here is where it gets ugly. Made uglier by the fact that I am reviewing a proposed T/I in a core/shell which was previously approved using the info below for the "future" tenant.

Proposed structure is single occupant, one-story, IIB, partially sprinklered (more on that in a minute), 60' yards exist, they classify the greenhouse as F-2 (I suspect because their is no unlimited area provision for group U other than appx C). I think it should be U. The processing is proposed as F-2 (accurate), storage as S-2 (accurate) and office as B (accurate). Here are the numbers:
105,000² greenhouse
24,000sf² processing
6,000sf² storage
5,000sf² office

They propose that they are an unlimited area building per 507.3 for S-2 and F-2. They seem to ignore the B. There are no proposed rated separations. They propose to sprinkle everything but the greenhouse. They are proposing an accessory mixed use strategy based on the fact that under their proposal the F2 is 129,000sf² and the aggregate accessories total less than 10%. The greenhouse as a U changes that. If that is the case, I think the only mixed use option would require a separated strategy, which would require the B to be separated from the rest of the building (as a NS building since the whole building is not sprinklered). The proposed building was approved under the C/S and with a well-written AMMR allowing the unsprinkled greenhouse, albeit with the greenhouse as an F-2. If the appendix was adopted/used, I think they could have an unlimited area for the NS greenhouse, and no sprinkler requirements for any of the others, but the separation would still be required. If I point this out I will be contradicting the previous approval, and the criteria used in the AMMR.

At this point, I think the design could have been approved with an accurate assessment of the classification and mixed use strategy with a an AMMR that reflected these conditions if they didn't want the separation, and I am not eager to poke this bear in their already constructed building. So, if you can follow my saga at all, is there any guidance on it? Take it easy on me, this is my first pass at a project like this. The facility is NOT a cannabis facility.
 
Section 101.2.1 states "Provisions in the appendices shall not apply unless specifically adopted." Thus, in my opinion, the second part of Footnote 'i' of Table 506.2 is irrelevant if Appendix C is not adopted.

I read the reason statement for this proposal and it does not mention the conflict should Appendix C not be adopted. The committee approved the proposal as submitted, but also did not mention the Appendix C issue in their reason for approval. The Commentary is of no help, even though it does address that specific footnote--it just states that it "directs the code user to Appendix C."

The reasoning behind my opinion lies in this question: why do jurisdictions specifically adopt the IMC, IPC, IFC, IFGC, IPMC, IECC, and IEBC when, technically, all they need to do is adopt the IBC which references those standards? If a jurisdiction does not specifically adopt the IECC, but rather the NFPA energy code, and fails to modify Section 101.4.6, does that mean code users are still required to comply with the IECC along with NFPA 900? Most jurisdictions would only accept what they adopted.
 
MT, the greenhouse is not open to the public. The only occupants will be occasional maintenance on the automated conveyors.

RLGA, I agree, but had never encountered that footnote. I am wrestling with the adoption and references issue on another aspect of this project too. This facility utilizes a CO2 enrichment system, which is not addressed by the IBC as far as I know. However, it is addressed by the IFC. Since IBC 101.4 includes the language "to the prescribed extent of the each such reference" and I don't appear to have any prescribed extent in the IBC to get me there I wonder about using it. For now I am asking them to verify compliance with the relevant IFC sections since it is not an appendix, rather a referenced code.
 
IMO the previous shell was approved with the info on hand at the time. If they don't meet that its on them not you. I would treat it like any other Change of use/occ.
 
I found at that there was much conversation about the very issue I was most concerned about, and approved as an F2 instead of a U. They just did a terrible job of sharing that with me on the submittal. I received all the appropriate documentation so on that particular issue I am good.
 