Grilling on the 4TH
Rider Rick
Silver Member
3-29-2010 009.jpg7-4.jpg[/attachment:3hug78uq]A sprinkled 20 unit appartment building with a 1# propane tank gas grill on a combustible balcony without a sprinkler head.Under the 2006 IFC Section 308.3.1 & 308.3.1.1 would the above grill be allowed?Rick
/monthly_2010_08/572953db6756d_3-29-2010009.jpg7-4.jpg.ced93b035e9f3f4df21ccc1164453749.jpg
Re: Grilling on the 4TH
How many "grill" fires are from gas grills. I can understand a ban on charcoal grills and lighter fluids and 3 legged webers tipping over. A propane grill is no more a hazard than the gas stove inside the unit. From the looks of the baulaster spacing this building is a legacy code building (UBC) and if 16 units or less not sprinklered.
YesHow about natural gas grills can you find a restriction for them in the IFC?
The installation may be legal because its not connected to a 20 pound water capacity cylinder. The appliance appears to be using the 2.5 pound cylinder. However, under IFC Section 308.3.1.1, it sure looks like it's less than 10 feet from combustible construction (and I'm excluding the stand).
The key is the size of the LPG tank. If it is 2.5 pounds water capacity or less there is no restriction on its placement on balconies or within 10 ft of combustible construction.
308.3.1.1 Liquefied-petroleum-gas-fueled cooking devices.
LP-gas burners having an LP-gas container with a water capacity greater than 2.5 pounds [nominal 1 pound (0.454 kg) LP-gas capacity] shall not be located on combustible balconies or within 10 feet (3048 mm) of combustible construction.
Now how about the different definitions between a balcony and a deck?
201.3 Terms defined in other codes.
Where terms are not defined in this code and are defined in the International Building Code, International Fuel Gas Code, International Mechanical Code or International Plumbing Code, such terms shall have the meanings ascribed to them as in those codes.
IBC- BALCONY, EXTERIOR. An exterior floor projecting from and supported by a structure without additional independent supports.
IBC- DECK. An exterior floor supported on at least two opposing sides by an adjacent structure, and/or posts, piers or other independent supports.
Can't tell by the picture if the grill is an a deck or balcony.
Don't you just love the I-Codes
From the Washington State Fire Code
Code:
WAC 51-54-3800 Chapter 38--Liquefied petroleum gases.Section 3801.1 Scope. Storage, handling and transportation ofliquefied petroleum gas (LP-gas) and the installation of LP-gasequipment pertinent to systems for such uses shall comply with thischapter and NFPA 58. Properties of LP-gas shall be determined inaccordance with Appendix B of NFPA 58.EXCEPTION: The use and storage of listed propane fired barbeque grills on R-2 decks and balconies with an approved containernot exceeding a water capacity of 20 pounds (9 kg) that maintain a minimum clearance of 18 inches on all sides,unless listed for lesser clearances.
20 pounds and 18 inches are the thresholds.