• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Grounding & Bonding of Air-Conditioning and Refrigerating Equipment NEC 440.9

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,057
Location
Somewhere Too Hot & Humid
The NEC says this under 440.9:

440.9 Grounding and Bonding.
Where equipment is installed outdoors on a roof, an equipment grounding conductor of the wire type shall be installed in outdoor portions of metallic raceway systems that use compression-type fittings.

What it means is this:

Metal raceway systems with compression fittings listed for use in wet locations that are installed on rooftops to supply air-conditioning and refrigeration equipment could be subject to movement and physical damage. This is a result of rooftop activities such as snow removal or roof repair/replacement. These activities can lead to inadvertent separation of the raceway system, compromising the ground-fault return path. The installation of a wire-type equipment grounding conductor provides redundancy of the ground-fault return path to facilitate the operation of the circuit overcurrent protective device (OCPD) in the event of a line-to-ground fault at the air-conditioning or refrigeration equipment.
 