Grounds and Neutrals must be separated?

Darren Emery

REGISTERED
Joined
Oct 20, 2009
Messages
510
Location
Manhattan, Ks
What section of the IRC requires the grounds and neutrals to be separated, other than at the main bonding jumper in the service equipment? I have found the pertinent section in the NEC, but not in the IRC.
 
Last edited by a moderator:
if you can't find it in the text ( and i can't either, i hinge on E3301.1, last sentence in the paragraph. i use the NEC. any electriciain that doesn't know that at subpanels ( after first point of disconnect) grounds and nuetrals get seperated,and apply by that rule probably needs a quick lesson in parallel paths to ground
 
i found these shortly after I posted....

E3908.6 Load-side grounded conductor neutral. A

grounded conductor shall not be connected to normally

noncurrent-carrying metal parts of equipment, to equipment

grounding conductor(s), or be reconnected to ground on the

load side of the service disconnecting means.

E3908.7 Load-side equipment.Agrounded circuit conductor

shall not be used for grounding noncurrent-carrying metal

parts of equipment on the load side of the service disconnecting

means.
 
I have found the pertinent section in the NEC, but not in the IRC.
The IRC has a cross reference

APPENDIX Q

ICC INTERNATIONAL RESIDENTIAL CODE ELECTRICAL PROVISIONS/NATIONAL ELECTRICAL CODE CROSS-REFERENCE
 