mtlogcabin
SAWHORSE
Mt State ammendment
(38) Subsection 903.2.7, condition #4 is deleted and replaced with the following: "A Group M occupancy is used for the display and sale of upholstered furniture which exceeds 2500 square feet of display and sale area."
2012 IBC
903.2.7 Group M.
An automatic sprinkler system shall be provided throughout buildings containing a Group M occupancy where one of the following conditions exists:
1. A Group M fire area exceeds 12,000 square feet (1115 m2).
2. A Group M fire area is located more than three stories above grade plane.
3. The combined area of all Group M fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group M occupancy used for the display and sale of upholstered furniture or mattresses exceeds 5,000 square feet (464 m2)
I have a proposed 2,900 sq ft store displaying beds (mattresses) The architect is proposing a 510 sq ft 1 hour rated room to reduce the display area thus eliminating the sprinkler require in Mt. The room would be used as a "temporary" room for the wharehouse to drop off the mattresses for the customer to pick up the next day. They would be stored on there sides thus no storage above 6 ft.
Question how much Group A plastic is allowed below 6 ft before sprinklering is required? In other words can someone explain Section 2303.7.4 Limited quantities of Group A plastics in mixed commodities to me in laymens terms.
(38) Subsection 903.2.7, condition #4 is deleted and replaced with the following: "A Group M occupancy is used for the display and sale of upholstered furniture which exceeds 2500 square feet of display and sale area."
2012 IBC
903.2.7 Group M.
An automatic sprinkler system shall be provided throughout buildings containing a Group M occupancy where one of the following conditions exists:
1. A Group M fire area exceeds 12,000 square feet (1115 m2).
2. A Group M fire area is located more than three stories above grade plane.
3. The combined area of all Group M fire areas on all floors, including any mezzanines, exceeds 24,000 square feet (2230 m2).
4. A Group M occupancy used for the display and sale of upholstered furniture or mattresses exceeds 5,000 square feet (464 m2)
I have a proposed 2,900 sq ft store displaying beds (mattresses) The architect is proposing a 510 sq ft 1 hour rated room to reduce the display area thus eliminating the sprinkler require in Mt. The room would be used as a "temporary" room for the wharehouse to drop off the mattresses for the customer to pick up the next day. They would be stored on there sides thus no storage above 6 ft.
Question how much Group A plastic is allowed below 6 ft before sprinklering is required? In other words can someone explain Section 2303.7.4 Limited quantities of Group A plastics in mixed commodities to me in laymens terms.