NFPA 72 has this comment
Can you elaborate or provide a reference?
Let me look
Do you have access to NFPA 72??? And if so which editon
I guess I'm missing the whole point of having the audio messages for a fire alarm. I'm not sure what else they would say besides "There is a fire, evacuate the building". And it seems like that same message could be conveyed by the basic horn/strobes. I don't think this is intended to be used to announce other emergencies. And it also seems somewhat redundant since most schools already have some type of paging system.
With a voice evac, if set up correctly, there is supposed to be three rounds of the temoral three pattern, than the voice message. and that cycle repeats.
With a voice evac system, you also get a microphone at the panel. Yes it can be used for other emergencies. Kind of where these started out was in high rises, with an idea, you can talk to the entire building or select which floors you may want to convey a specific message to.
The voice evac/ fire alarm is just a better designed system than most pa's , and has battery back up, if power goes out.
And just for background, this is an existing school with an existing FA system. But they need a fire alarm panel replacement, and looks like NFPA requires the annunciators to be upgraded when the panel is replaced.
Now this is an AHJ question, unless the contract, or school district wants a voice evac.
If it is just a panel replacement, sometimes you can get away with just that, and not repleace any other components.