Sifu
- Joined
- Sep 3, 2011
- Messages
- 3,391
Given a single story, VB, NS building housing individual private garages, each < 1000sf². The layout is 11 bays across, back to back for a total of 22 bays. 2018 IBC 406.3.1 requires them to be classified a group U and to be separated from each other by 1-hr fire barriers. 707.5 requires the fire barriers to terminate at the underside of the roof sheathing, slab or deck above. There is no allowance I see to terminate them at a rated horizontal assembly in this case. I have a proposal to stop the fire barriers at a rated horizontal assembly, and proceed with draftstopping per 718.4 from the top of the fire barrier through the attic at every 3'000sf². So the garage bays are separated by fire barriers from each other, and by a horizontal assembly from the attic spaces above, but the fire barriers do not provide the continuity required of them by 707.5. It SEEMS like there is a path for this (I think I found it last time I faced this) but I can't find it now. Any thoughts?