Can someone point to where either IBC or NFPA Life Safety code says you don't need a guardrail or handrail when the total rise of the stair is less than 30"? I know it's out there somewhere and I've googled and found a couple posts, but nothing that says in plain English, if its exactly 30" or less, you don't need a guardrail.
Anyone know?
Handrails per the CBC1009.15 Handrails. Stairways shall have handrails on each
side and shall comply with Section 1012.
I hope this helps
Guards per the CBC
1013.2 Where required. Guards shall be located along opensided
walking surfaces, including mezzanines, equipment
platforms, stairs, ramps and landings that are located more
than 30 inches (762 mm) measured vertically to the floor or
grade below at any point within 36 inches (914 mm) horizontally
to the edge of the open side. Guards shall be adequate in
strength and attachment in accordance with Section 1607.8.
Exception: Guards are not required for the following locations:
1. On the loading side of loading docks or piers.
2. On the audience side of stages and raised platforms,
including steps leading up to the stage and raised
platforms.
3. On raised stage and platform floor areas, such as
runways, ramps and side stages used for entertainment
or presentations.
4. At vertical openings in the performance area of
stages and platforms.
5. At elevated walking surfaces appurtenant to stages
and platforms for access to and utilization of special
lighting or equipment.
6. Along vehicle service pits not accessible to the public.
7. In assembly seating where guards in accordance
with Section 1028.14 are permitted and provided.
Handrails per the CRCR311.7.8 Handrails. Handrails shall be provided on at
least one side of each continuous run of treads or flight
with four or more risers.
ICE is right, but please note the difference between "guardrail" and "handrail", as they are often two separate things with different functions:
- Guardrail (IBC 1013) helps keep you from falling from the upper space, over the edge and into the space below. No hands needed.
- Handrail (IBC 1012, and also the accessibility code for ramps and stairs) keeps you from stumbling and helps you use your hands to get up and down stairs and ramps as you transition between the two elevations.
The code requirements for handrails in section 1012.1 and 1009.15 have nothing directly to do with 30 inches height.
For example, in a public space, you could have a 14" elevation change between two levels, and have a stair with two 7" risers and one 11" tread: that stair would require handrails, but not a guardrail.
Or, you could have a 35" elevation change between two levels, and have a monumental walkway [like a long, low series of garden steps] with five 7" risers separated by four 44" "landings": that would require guardrail, but no handrails (1009.15 exc. #3).
rbcameron1 said:
Can someone point to where either IBC or NFPA Life Safety code says you don't need a guardrail or handrail when the total rise of the stair is less than 30"? I know it's out there somewhere and I've googled and found a couple posts, but nothing that says in plain English, if its exactly 30" or less, you don't need a guardrail.Anyone know?
Commercial or residential?
R312.1 Where required. Guards shall be located along open-sided walking surfaces, including stairs, ramps and landings, that are located more than 30 inches (762 mm) measured vertically to the floor or grade below at any point within 36 inches (914 mm) horizontally to the edge of the open side. Insect screening shall not be considered as a guard.
1015.2 Where required. Guards shall be located along
open-sided walking surfaces, including mezzanines, equipment
platforms, aisles, stairs, ramps and landings that are
mm) horizontally to the edge of the open side. Guards shall
be adequate in strength and attachment in accordance with
Section 1607.8.
2015 IBC Section 1011.11 Handrails. Stairways shall have handrails on each
side and shall comply with Section 1014. Where glass is used
to provide the handrail, the handrail shall comply with Section
2407.
1. Stairways within dwelling units and spiral stairways
are permitted to have a handrail on one side only.
2. Decks, patios and walkways that have a single
change in elevation where the landing depth on each
side of the change of elevation is greater than what
is required for a landing do not require handrails.
3. In Group R-3 occupancies, a change in elevation
consisting of a single riser at an entrance or egress
door does not require handrails.
4. Changes in room elevations of three or fewer risers
within dwelling units and sleeping units in Group R-
2 and R-3 do not require handrails.