Does this mean that a fall arrest/restraint cannot take the place of guards on a flat roof since a flat roof does not have a hip and ridge?
1015.7 Roof access. Guards shall be provided where the roof
hatch opening is located within 10 feet (3048 mm) of a roof
edge or open side of a walking surface and such edge or open
side is located more than 30 inches (762 mm) above the floor,
roof or grade below. The guard shall be constructed so as to
prevent the passage of a sphere 21 inches (533 mm) in diameter.
Exception: Guards are not required where permanent fall
arrest/restraint anchorage connector devices that comply
with ANSI/ASSE Z 359.1 are affixed for use during the
entire roof covering lifetime. The devices shall be reevaluated
for possible replacement when the entire roof covering
is replaced. The devices shall be placed not more than
10 feet (3048 mm) on center along hip and ridge lines and
placed not less than 10 feet (3048 mm) from the roof edge
or open side of the walking surface.
1015.7 Roof access. Guards shall be provided where the roof
hatch opening is located within 10 feet (3048 mm) of a roof
edge or open side of a walking surface and such edge or open
side is located more than 30 inches (762 mm) above the floor,
roof or grade below. The guard shall be constructed so as to
prevent the passage of a sphere 21 inches (533 mm) in diameter.
Exception: Guards are not required where permanent fall
arrest/restraint anchorage connector devices that comply
with ANSI/ASSE Z 359.1 are affixed for use during the
entire roof covering lifetime. The devices shall be reevaluated
for possible replacement when the entire roof covering
is replaced. The devices shall be placed not more than
10 feet (3048 mm) on center along hip and ridge lines and
placed not less than 10 feet (3048 mm) from the roof edge
or open side of the walking surface.