• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

"H". and Smoke vents

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
A local area code admendment group is proposing requiring automatic smoke vents in "H" over 10000 sq ft. With links 100 degrees above the sprinkler head

Any thoughts good bad????
 
Peach is it a good design though??

Say automatic vents over a sprinklered flammable storage room????
 
Not sure that many fusible link options exist that are listed for smoke and heat vents to meet all temperature ranges of sprinkler heads by a 100 degree increment.

165 and 212 tend to stick out in my mind, not sure what they offer today.

http://www.bitorq.com/pdfs/fusible_links/link_temperatures.pdf

Also, what would happen in a few years if FM or UL testing indicated that vents had a negitive impact on the sprinkelr system operation such as ESFR sprinkler systems...... Better to leave the S & H automatic vents as a designer's option. (LIABILITY)

If FD ops want the vents installed, require manually operated S&H vents, and remove the automatic operation of these vents.
 
That is what I an thinking

Depending on where the head is located, seems the vent may open before or close to the head going off

And also say you have a flammable storage room on fire and the vents open, may have a nice candle coming out of the top
 
Seems like depending on location of sprinkler head in relation to the vent

If the head is going off around 200, and the vent is higher up then the head, seems like the vent is going to go not much after that.

When ceiling temps are reaching 1000
 
Below is from FM Global Property Loss Prevention Data Sheets 2-0 January 2011. Why not go with an organization that has done full scale testing on this instead of guessing???

2.1.1.7.1 Heat and/or Smoke Vents

Do not install automatic smoke and heat vents in facilities equipped with sprinkler protection; manual heat

and smoke vents, however, are acceptable. If local codes require the installation of automatic smoke and heat

vents, do one of the following:

(a) Install vents that are FM Approved for occupancies protected by quick-response Storage sprinklers.

(b) Install FM Approved vents equipped with a standard-response 360°F (182°C) nominal thermal

activating device.

© Install quick-response sprinklers directly under the vent opening on a maximum 4 ft (1.2 m) linear and

16 ft2 (1.5 m2) area spacing. Position the centerline of the sprinkler’s thermal element in accordance with

the guidelines outlined in Section 2.1.3.2.4. Ensure these sprinklers have, at a minimum, the same

K-factor and orientation as the adjacent ceiling-level sprinklers and are fed by sprinkler piping no smaller

than the ceiling level branchlines. Sprinklers located under the ceiling vent and installed as outlined above

do not need to be added to the hydraulic design of the ceiling sprinkler system. See Figure 1a for a

diagram of this arrangement.
 
ok some reason it was added in the 2003 IFC 910.2.2 and taken out of the 2009 IFC, make that it was taken out of the 2006 IFC

anyone have the reason it was taken out of the 2006??????????????
 
Last edited by a moderator:
We had an account that had mechanical vents held in the shut position by fusible links. The smoke detector, by a relay, sent voltage to a fusible link. The voltage melted the solder, the links fell out and the 6 foot x 6 foot vents popped open. The first time we tested the FA, no one told us about the links. We had to gather all the solder we could find and have the links soldered together. Then it took 4 guys to hold the vents closed while the links were installed. We never tested that smoke detector again. But, in case of fire, the stage would have been vented quickly.

http://www.globetechnologies.com/
 
ok some reason it was added in the 2003 IFC 910.2.2 and it was taken out of the 2006 IFC

anyone have the reason it was taken out of the 2006??????????????
 