Below is from FM Global Property Loss Prevention Data Sheets 2-0 January 2011. Why not go with an organization that has done full scale testing on this instead of guessing???
2.1.1.7.1 Heat and/or Smoke Vents
Do not install automatic smoke and heat vents in facilities equipped with sprinkler protection; manual heat
and smoke vents, however, are acceptable. If local codes require the installation of automatic smoke and heat
vents, do one of the following:
(a) Install vents that are FM Approved for occupancies protected by quick-response Storage sprinklers.
(b) Install FM Approved vents equipped with a standard-response 360°F (182°C) nominal thermal
activating device.
© Install quick-response sprinklers directly under the vent opening on a maximum 4 ft (1.2 m) linear and
16 ft2 (1.5 m2) area spacing. Position the centerline of the sprinkler’s thermal element in accordance with
the guidelines outlined in Section 2.1.3.2.4. Ensure these sprinklers have, at a minimum, the same
K-factor and orientation as the adjacent ceiling-level sprinklers and are fed by sprinkler piping no smaller
than the ceiling level branchlines. Sprinklers located under the ceiling vent and installed as outlined above
do not need to be added to the hydraulic design of the ceiling sprinkler system. See Figure 1a for a
diagram of this arrangement.