H occupancy perimeter exterior wall access

chris macko

REGISTERED
Joined
Dec 3, 2021
Messages
25
Location
Chicago
I've got a building with a 2 story mixer area and related staging and support spaces that will all be classified as H-3 (Class IIIA flammable liquids), as well as an identical suite of mixers and support that will be H-4 (highly toxic) next to it, separated by a rated egress passageway. Per 415.6, H-3 and H-4 occupancies need to have 25% of the perimeter on an exterior wall. In the case of multiple rooms within the same occupancy, and multiple types of H occupancy, how would you define those areas for measurement? Is all the H area looked at as a whole compared to the overall perimeter? Are H-3 and H-4 areas broken out separately? Is each specific mixer and storage room required to have its own exterior wall access?
It matters in this case because the common walls between different H areas add to that perimeter requirement for the exterior walls, so areas that will work if treated as whole, will not work if broken out into smaller areas. I think in this case the rated egress passage between them does force a separation, but there's still a question over how much of the rest of the spaces get grouped.
 
Section 415.6 states, "...25 percent of the perimeter of the occupancy..."

This would apply to the Group H3 occupancy only. So if the building has a 1,000-foot perimeter, and the Group H-3 occupancy has a 400-foot perimeter, then you would need to have 100 feet of the Group H-3 on an exterior wall.
 