• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Handrail for stadium seating

Joined
Oct 19, 2009
Messages
516
Location
Lincoln
Applicable code:2012 IBC Chapter 10, handrails.There is a proposal to have an open assembly area within a larger office area to have stadium seating. There is one access aisle on one side only with only hand rail. Normally a handrail is required on BOTH sides of a stairway but it is common that end aisles serving stadium seating for movie theaters will have one hand rail running along the half-high wall. In this scenario, we are missing the upholstered seats.Does anyone provide a definitive answer whether-or-not the handrails sketched in red-yellow would be needed?See attachment.Happy Holidays!ICC Certified Plan ReviewerNFPA Certified Fire Plan Examiner

View attachment 2169

View attachment 2169

/monthly_2015_12/Handrails.jpg.e8a95790af401a7c635d011db8956ed3.jpg
 
Not an ibc person

But with the stairs seems like the answer is yes,

Not only for handrail but so you do not walk off the stairs onto the seating area
 
Only the one handrail is required per Section 1028.13 (2012 IBC). The configuration you show is very similar to a bleacher or grandstand, which are regulated by ICC 300. Although not technically a bleacher or grandstand by definition (definition requires them not to be a element of a building), ICC 300 requires only one handrail on the non-seating side, which is comparable to the requirement in the IBC. Therefore, I do not think the added handrails you show are required.
 
@ ~ ~ @



Section 1028.13, Exception # 2 seems to indicate that handrails

would not be required.

From Section 1028.13, Ex. # 2:

2."Handrails are not required if, at the side of the aisle, there is

a guard that complies with the graspability requirements of

handrails."



@ ~ ~ @
 
RLGA said:
Only the one handrail is required per Section 1028.13 (2012 IBC). The configuration you show is very similar to a bleacher or grandstand, which are regulated by ICC 300. Although not technically a bleacher or grandstand by definition (definition requires them not to be a element of a building), ICC 300 requires only one handrail on the non-seating side, which is comparable to the requirement in the IBC. Therefore, I do not think the added handrails you show are required.
Could see code does not require a handrail,,

But what about a "guard" so if you are on one of the two stairs, a person does not step down to the actual seating level, and bust their head???
 
Head busting is permitted according to IBC 1013.2. Guard rails not required along the open-sided walking surface (including stairs) where the vertical surface below is less than 30 inches.
 
BayPointArchitect said:
Head busting is permitted according to IBC 1013.2. Guard rails not required along the open-sided walking surface (including stairs) where the vertical surface below is less than 30 inches.
OK, go forth and build

Maybe the lawsuit would make them required?? but anyway
 
cda said:
OK, go forth and buildMaybe the lawsuit would make them required?? but anyway
I agree that both:

- the handrail is not required

- a busted head is quite likely to happen.

It is a clever idea to have what appears to be a main exit POT from the second floor become part of an aisle exit system... perhaps a bit too clever...?
 