• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Head loss in 610.8(2) vs. A104.2

AnnDee4444

Registered User
Joined
Jun 23, 2020
Messages
1
Location
California
Both of the below code sections are from the 2016 California Plumbing Code. They can't seem to decide how much psi to subtract for elevation gain. Anyone have any insight on this?

610.8 Size of Meter and Building Supply Pipe Using Table 610.4
(2): Add or subtract depending on positive or negative elevation change, 1/2 psi (3.4 kPa) for each foot (305 mm) of difference in elevation between such source of supply and the highest water supply outlet in the building or on the premises.

A104.2 Elevation.
Determine the elevation of the highest fixture or group of fixtures above the water (street) main. Multiply this difference in elevation by 0.43. The result is the loss in static pressure in psi (kPa).
 
0.43 is correct. 1/2 is probably a rounded number, since it's easier for most people to divide by 2 than multiply by 0.43 in their heads.
 