I have an old project where the original photoluminescent exit signs are no longer keeping their 90 minute illumination requirement, so they did not pass annual fire department inspection. The signs did have a label saying they complied with UL 924, and the original manufacturer had an ICC report at time of installation.
Upon further investigation, it appears that the owner had recently retrofitted the hallway lighting from fluorescent to LED. The new LED do not put out as much of the UV light spectrum energy, so the photoluminescent material in the signs is no longer fully charging.
File this one under "unintended consequences".