PatrickGSR94
Member
I have a church building, Group A-3, Type II-B construction, 2 stories, fully sprinkled, open space all around. It's had several previous additions, and is currently near the limit of of mixed-use nonseparated, at ~31,000 SF per floor (35,625 allowed with multi-story sprinkler and frontage increases). Addition will add about 7,500 SF.
I ran the numbers on the different occupancies and areas, and if the new addition is done as mixed-use Separated (with no separation required between E and A, 1-hour between E/A and B), the weighted average comes out to 0.99 with the addition, IF it's all done as Type II-B to match the existing building.
However we're looking at doing the addition in heavy timber as Type IV. Even though Type II is a "higher" building type, IV actually allows more area. But if the entire building's weighted averages comes out to less than 1.0 as Type II, could we do the addition as Type IV without needing a 3-hour fire wall?
I ran the numbers on the different occupancies and areas, and if the new addition is done as mixed-use Separated (with no separation required between E and A, 1-hour between E/A and B), the weighted average comes out to 0.99 with the addition, IF it's all done as Type II-B to match the existing building.
However we're looking at doing the addition in heavy timber as Type IV. Even though Type II is a "higher" building type, IV actually allows more area. But if the entire building's weighted averages comes out to less than 1.0 as Type II, could we do the addition as Type IV without needing a 3-hour fire wall?