2012 IBC type II construction
Can someone tell me what they mean in 2.1 "lower roof assembly"? Are they referring to the supporting structure? I don't see any guidance in the commentary. Does this in anyway eliminate the need for fireproofing on one side or the other of the firewall on the underside of the roof deck if you have an uneven roof?
This is an exception we may want to use to eliminate the need for a parapet for a firewall on an addition to an existing church to eliminate the requirement for sprinkling.
706.6 Vertical continuity.
Fire walls shall extend from the foundation to a termination point at least 30 inches (762 mm) above both adjacent roofs.
Exceptions:
2. Two-hour fire-resistance-rated walls shall be permitted to terminate at the underside of the roof sheathing, deck or slab, provided:
2.1. The lower roof assembly within 4 feet (1220 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour.
2.2. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall.
2.3. Each building shall be provided with not less than a Class B roof covering.
BSSTG
2012 IBC type II construction
Can someone tell me what they mean in 2.1 "lower roof assembly"? Are they referring to the supporting structure? I don't see any guidance in the commentary. Does this in anyway eliminate the need for fireproofing on one side or the other of the firewall on the underside of the roof deck if you have an uneven roof?
This is an exception we may want to use to eliminate the need for a parapet for a firewall on an addition to an existing church to eliminate the requirement for sprinkling.
706.6 Vertical continuity.
Fire walls shall extend from the foundation to a termination point at least 30 inches (762 mm) above both adjacent roofs.
Exceptions:
2. Two-hour fire-resistance-rated walls shall be permitted to terminate at the underside of the roof sheathing, deck or slab, provided:
2.1. The lower roof assembly within 4 feet (1220 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour.
2.2. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall.
2.3. Each building shall be provided with not less than a Class B roof covering.