Yeah, Yeah, I know we have beat this thing to death... Please assist.
2012 I Codes. WA State amendments.
Commercial pizza oven, extra heavy duty, uses wood as part of heat source. 70" diameter oven.
MFGR's installation instructions; Note 2 venting options provided neither of which appear to be code compliant.
www.earthstoneovens.com/media/pdf/EarthStone_Venting_Commercial.pdf
Typical questions, Do I need a hood? Can it be an eyebrow hood?
I guess my issues here are why the departure between NFPA 96 and the IMC? If ICC is going to reference NFPA for everything known to man then why in this case do they not have the same allowances?
IMC section 507.13.1 clearly does not allow eyebrow type hoods for extra heavy duty appliances. NFPA 96 does not appear to restrict their use as long as they can capture the smoke and grease laden fumes.
NFPA 96 Section 14.7.4 seems to allow direct venting of the appliance when the firebox is solid masonry or refractory type materials, although they do not specify thickness. IMC seems silent about the issue.
Instead of writing code sections that say "where approved by the AHJ", (NFPA 14.7.4) which obviously is the whole premise of code to start with, they need to provide conditions acceptable to gain that approval or leave that wording out of the code section.
Anyhow, if you can indulge me again with any and all knowledge regarding this application it would be greatly appreciated. I'm not seeing an allowance in the IMC for either of the manufacturers listed installation methods.
Thanks,
ZIG
2012 I Codes. WA State amendments.
Commercial pizza oven, extra heavy duty, uses wood as part of heat source. 70" diameter oven.
MFGR's installation instructions; Note 2 venting options provided neither of which appear to be code compliant.
www.earthstoneovens.com/media/pdf/EarthStone_Venting_Commercial.pdf
Typical questions, Do I need a hood? Can it be an eyebrow hood?
I guess my issues here are why the departure between NFPA 96 and the IMC? If ICC is going to reference NFPA for everything known to man then why in this case do they not have the same allowances?
IMC section 507.13.1 clearly does not allow eyebrow type hoods for extra heavy duty appliances. NFPA 96 does not appear to restrict their use as long as they can capture the smoke and grease laden fumes.
NFPA 96 Section 14.7.4 seems to allow direct venting of the appliance when the firebox is solid masonry or refractory type materials, although they do not specify thickness. IMC seems silent about the issue.
Instead of writing code sections that say "where approved by the AHJ", (NFPA 14.7.4) which obviously is the whole premise of code to start with, they need to provide conditions acceptable to gain that approval or leave that wording out of the code section.
Anyhow, if you can indulge me again with any and all knowledge regarding this application it would be greatly appreciated. I'm not seeing an allowance in the IMC for either of the manufacturers listed installation methods.
Thanks,
ZIG