• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Higher temp sprinkler heads in coolers and freezers????

Simonsays

Registered User
Joined
Mar 2, 2010
Messages
68
Really NFPA? According to NFPA 13-8.3.2.5 #10, sprinkler heads in walk-in coolers and freezers equipped with automatic defrosting shall be of the intermediate (175 degree) temperature classification or higher. Come on! "The heat from the defrost unit can approach 165 F." How often does this occur? Sounds like an area of interest for our energy-concious friends. All right people, let me hear your common sense response
 
Follow the good book! Most folks have not adopted the 2010 edition of 13 and will not have to deal with it for a while. I do not see a big deal with the higher temperature of the head. I am sure the NFPA 13 committee saw a few loses as a result of the higher temperature and made the change.
 
It sounds like a blanket requirement for a specific problem. There very well may be an electric defrost on low temp freezers, but not on all coolers. Why the blanket? Perhaps to draw a line somewhere and avoid judgment calls.
 