IBC 2006 – Auditorium building Type I B construction one story with three mezzanine levels. To comply with egress requirements for exit width the designer is proposing a horizontal exit on the third mezzanine level(two other vertical exits are provided). Horizontal exit is being established by a 2 hour rated corridor as the fire compartment with exits one on each side of the long corridor. One vertical exit stair 2 hour rating enclosure is leading to outside and the second is 1 hour rated enclosure leading into the lobby area which leads to the outside.
My question is when the corridor is used as the fire compartment/ horizontal exit I am finding it challenging to calculate number of exits and exit width since we can not count the occupant exiting through the horizontal exit. I can use dead end corridor to establish exit on each side of corridor the question then is would the second stairs exiting through lobby complies? I do understand that the horizontal exit is an area of refuge what factor would we use to establish minimum area required for this area of refuge I am reading 3 square feet per occupant.
One more question Section 1022.2 Separation states below the exception “Horizontal exit walls constructed as fire barriers shall be continuous from exterior wall to exterior wall so as to divide completely the floor served by the horizontal exit.” I read this as part of the requirement however placement under the exception makes the language more part of the exception???
Any help or comments are appreciated ideas??
My question is when the corridor is used as the fire compartment/ horizontal exit I am finding it challenging to calculate number of exits and exit width since we can not count the occupant exiting through the horizontal exit. I can use dead end corridor to establish exit on each side of corridor the question then is would the second stairs exiting through lobby complies? I do understand that the horizontal exit is an area of refuge what factor would we use to establish minimum area required for this area of refuge I am reading 3 square feet per occupant.
One more question Section 1022.2 Separation states below the exception “Horizontal exit walls constructed as fire barriers shall be continuous from exterior wall to exterior wall so as to divide completely the floor served by the horizontal exit.” I read this as part of the requirement however placement under the exception makes the language more part of the exception???
Any help or comments are appreciated ideas??