A hotel room without cooking provisions is not a dwelling unit, therefore tamper resistant receptacles are not required. Am I correct?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Chapter 4 Equipment for General Use :: ARTICLE 406 Receptacles, Cord Connectors, and Attachment Plugs (Caps)jar546 said:A hotel room without cooking provisions is not a dwelling unit, therefore tamper resistant receptacles are not required. Am I correct?
God catch!georgia plans exam said:406.13 2011 NEC requires them for guest rooms and guest suites.GPE.