MakeNoAssumptions
REGISTERED
Hi All,
I am trying to figure out if we can use 1/2hr fire partitions to separate hotel rooms from each other and corridors. My code review says it is fine but everyone I talk to says they always just do 1-hr.
Building is fully sprinklered IIB and here are the sections that lead me to a 1/2 hr rating:
I am trying to figure out if we can use 1/2hr fire partitions to separate hotel rooms from each other and corridors. My code review says it is fine but everyone I talk to says they always just do 1-hr.
Building is fully sprinklered IIB and here are the sections that lead me to a 1/2 hr rating:
- 2015 IBC:
- Table 1020.1 allows 1/2hr corridors
- Section 708.3 allows 1/2hr in sprinklered building
- 2015 NFPA: 28.3.6.1.3
- 28.3.6.1.3 allows 1/2hr corridors
- 28.3.7.2 allows 1/2 guest room separation