Hotel Vanities
Jmb
PA
I know this has been covered in the past but I have one question in regards to vanity countertops in R1, Hotels:
Codes: IBC 2015, Chapter 11, ANSI A117.1-2009.
Here is the code section in question:
A117.1-2009: 1002.11.2.1 Vanity Counter Top Space. If vanity
counter top space is provided in dwelling or sleeping
units not required to be Accessible units within
the same facility, equivalent vanity counter top
space, in terms of size and proximity to the lavatory,
shall also be provided in Accessible units.
The the hotel has:
Non-accessible King Room with 10'-0" vanity
Non-accessible Queen Room with 7'-0" vanity
Non-accessible Double Room with 5'-0" vanity​
Question is do all of the Accessible Units, King , Queen, and Double, need a 10'-0" vanity since this is the longest counter in the "same facility" or is it based on each class of unit (i.e: accessible double needs only a 5'-0" vanity since the non-accessible double is 5'-0")
Thanks for any input
FACILITY. All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site.
King for King 10' vanity
Queen for Queen 7' vanity
Double for double 5' vanity
this would be inline with the definition intent of providing portion (space) for portion (space) compliance.
Jmb,
To add to the mix, if the non-Accessible King, Queen
& Double Rooms have a particular sized Vanity, then
to be ADA compliant [ and consistent ], those same
sizes must be provided in the Accessible Rooms.