annoyitated
SAWHORSE
The original building permit application was made in 1989 so I am assuming it was constructed utilizing the 1987 BOCA code which would have been adopted by the City at that time. According to the permit, it is a type 2A construction which allowed 5 Stories, 65 feet, and 19,950 allowable square feet for an A-3 Assembly Use.
With the sprinkler and open perimeter modifications, using 1987 BOCA calculations, the allowed height and areas increased to 6 Stories (+1st for A.S.), 85 feet (+20 feet for A.S.), and 56,977 allowable square feet (15% Area Reduction for 5 story building = 16,957.5 + 16957.5 for A.S. + 23,062.2 for open perimeter).
The building is a six floor building with a ground floor footprint of 41,132 square feet.
We are looking to add two additions to the building and are evaluating our options from a code perspective.
If I calculate the existing building allowable height and area using the 2009 IBC I get 4 stories (3 allowable per Table 503+1 for A.S.), 85 feet (65 feet allowable per Table 503 + 20 feet for A.S.), and 57,040 allowable square feet (15,500 allowable per Table 503 + 31,000 for A.S. + 10, 540 for open perimeter).
Currently, we exceed the 57,040 allowable square feet with our additions on at least one floor. As I investigate ways to tackle this problem, including the obvious one of reducing the additions, I was working through the 2009 IEBC options. In looking at the compliance methods I was leaning toward the Work Area Compliance Method since it allowed the use of a fire separation wall, my thinking was similar to a separated mixed-use. I have two questions that I can’t seem to find an answer to.
Question No. 1 – On my first level I have an A-3 existing on one side of the separation and an A-3 new on the addition side, is the rating really 0-hr?
Question No. 2 – If I construct the addition utilizing IB type construction it would allow 11 stories with unlimited area. With the existing building being 2A it is causing me a problem because some of the assembly ratings were only 1-1/2 hour and so I am guessing the AHJ will only allow that building to be considered a IIA equivalent (1-hr assembly ratings). So my problem is that I have a IIA with an allowable area of 57,040 square feet on one side of the fire separation and an unlimited allowable area with the IB on the other side. How do you calculate the Unity Formula (Mixed-Area Ratio) with an unlimited area?
With the sprinkler and open perimeter modifications, using 1987 BOCA calculations, the allowed height and areas increased to 6 Stories (+1st for A.S.), 85 feet (+20 feet for A.S.), and 56,977 allowable square feet (15% Area Reduction for 5 story building = 16,957.5 + 16957.5 for A.S. + 23,062.2 for open perimeter).
The building is a six floor building with a ground floor footprint of 41,132 square feet.
We are looking to add two additions to the building and are evaluating our options from a code perspective.
If I calculate the existing building allowable height and area using the 2009 IBC I get 4 stories (3 allowable per Table 503+1 for A.S.), 85 feet (65 feet allowable per Table 503 + 20 feet for A.S.), and 57,040 allowable square feet (15,500 allowable per Table 503 + 31,000 for A.S. + 10, 540 for open perimeter).
Currently, we exceed the 57,040 allowable square feet with our additions on at least one floor. As I investigate ways to tackle this problem, including the obvious one of reducing the additions, I was working through the 2009 IEBC options. In looking at the compliance methods I was leaning toward the Work Area Compliance Method since it allowed the use of a fire separation wall, my thinking was similar to a separated mixed-use. I have two questions that I can’t seem to find an answer to.
Question No. 1 – On my first level I have an A-3 existing on one side of the separation and an A-3 new on the addition side, is the rating really 0-hr?
Question No. 2 – If I construct the addition utilizing IB type construction it would allow 11 stories with unlimited area. With the existing building being 2A it is causing me a problem because some of the assembly ratings were only 1-1/2 hour and so I am guessing the AHJ will only allow that building to be considered a IIA equivalent (1-hr assembly ratings). So my problem is that I have a IIA with an allowable area of 57,040 square feet on one side of the fire separation and an unlimited allowable area with the IB on the other side. How do you calculate the Unity Formula (Mixed-Area Ratio) with an unlimited area?