Type V-A wood framed apartment building with cantilevered balconies. The balconies use membrane protection (type X gyp) to protect the underside of their framing with a 1 hour fire rating
California Building Code 2034.12.2.6 requires the cavities between the cantilevered joist to be ventilated at a ratio of 1/150th of the floor area.
I was initially thinking of doing this with a continuous soffit-type vent like we use at eaves, but does this soffit vent allow fire to actually bypass and defeat the 1 hour membrane protection?