• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

How to Calculate Non-Separated Use w/H Occupancy

Markmax33

Bronze Member
Joined
May 15, 2012
Messages
51
Location
San Diego CA
I was reading the building code today and trying to calculate the non-separated option for a building with multiple occupancies. The exception says, "H-2, H-3...shall be separated from all other occupancies in accordance with 508.4."

Which of the following are true:

1. This means that the non-separated use is calculated with the H-Occupancy floor area BUT the H-occupancy portions are separated.

2. This means that floors with H-occupancies cannot use non-separated use at all and must be calculated as separated. (This is what the code commentary book says!)

3. This means that the H-occupancies must be separated, but you the non-separated ratio is calculated upon the next most restrictive floor area and the ratio for the h-occupancy uses the h floor area.

A-2 occupancy B occupancy F-2 occupancy H-2 occupancy M occupancy

Aa = 13,395 ft2 Aa = 32,430 ft2 Aa = 32,430 ft2 Aa = 9,870 ft2 Aa = 17,625 ft2

Floor areas:

Floor A-2 Floor Area A-2 Ratio B Floor Area B Ratio F-2 Floor Area F-2 Ratio H-2 Floor Area H-2 Ratio M Floor Area M Ratio

3 31,321 ft2 2.338 3,210 ft2 0.24 3,210 ft2 0.24 8,000 ft2 0.597 1,532 ft2 0.114

2 1,351 ft2 0.101 35,135 ft2 2.623 3,513 ft2 0.262 6,555 ft2 0.489 35,135 ft2 2.623

1 3,456 ft2 0.258 80,000 ft2 5.972 531 ft2 0.04 533 ft2 0.04 1,531 ft2 0.114

Thanks! - Mark
 
A-2, B, F-2 and M can be one fire area (no-separated), each a fire area (separated) or a mixed of the two. The Group H-2 has to be separated (in its individual fire area)

Occupancy Group Allowable Area(from your post)

A-2 occupancy 13,395 sq ft

B occupancy 32,430 sq ft

F-2 occupancy 32,430 sq ft

M occupancy 17,625 sq ft

H-2 occupancy 9,870 sq ft (7,000 + 2,870)

H-2 can not exceed allowable area=9,870 sq feet

If you use non-separated (all occupancies except H-2) the most restrictive is Group A-2 so allowable area =13,395 sq ft

Actual area of mixed occupancy/13,395 + Actual Area of H-2 /9,870 ≤ 1
 
I didn't understand any of what you two just posted... and I teach the stuff!

Markmax33, what was that mishmash of numbers and letters at the end of your post?

In order to go non-separated you simply apply most restrictive area for all the various uses.

If you max out the non-separated area allowance you will need to create a separate fire area for the H use.

Sum of the ratios for separated uses won't work as your non-separated side is already at a value of 1.
 
The issue is the code does not permit all occupancies to exist together in nonseparated harmony. It specifically prohibits Group H from being a nonseparated occupancy (NSO).

The OP is seeking to have a mixed use building with Group H, but meeting the separated occupancy (SO) provision for the Group H area while the remaining mixed uses apply the nonseparated use provision.

The trick is, it's a little unclear how to mix and match SO and NSO, though there is a complimentary logical approach.

From the Commentary:

When one or more of the occupancies is a Group H-2, H-3, H-4 or H-5 high-hazard occupancy, the nonseparated occupancies option could not be applied for the Group H portions of the building (Exception 1). Any Group H occupancies would need to be separated as required by Section 508.4 for separated occupancies.
I read that the NSO can be applied to the remainder of the building, outside the Group H portions of the building. Therefore, the commentary does appear to support such an approach.We've sought to apply a similar weighted mix and match approach to address the MAQ of hazardous material storage in and out of cabinets within a common control area.
 