How to Connect NM Cable (Romex) to Knob and Tube

Commish, It appears the grounding wire is bent out of the way.

I think I prefer the connection in a junction box, realizing there is additional cost.

Is that #14ga ROMEX on a 15am fuse?

What gauge wire is the Knob-n-Tube, #12ga copper? Is it always assumed KNT is 12ga CU or does the inspector puts a wire gage on it?
 
I see that it is bent out of the way, to complete the hack the ground has to be cut off so the when the N & T is upgraded to a current y allowed conductors they have to replace the existing romex
 
I do not see anything that allows that connector without a box/enclosure
334.40 Boxes and Fittings.



(A) Boxes of Insulating Material.


Nonmetallic outlet boxes shall be permitted as provided by 314.3.

(B) Devices of Insulating Material.


Self-contained switches, self-contained receptacles, and nonmetallic-sheathed cable interconnector devices of insulating material that are listed shall be permitted to be used without boxes in exposed cable wiring and for repair wiring in existing buildings where the cable is concealed. Openings in such devices shall form a close fit around the outer covering of the cable, and the device shall fully enclose the part of the cable from which any part of the covering has been removed. Where connections to conductors are by binding-screw terminals, there shall be available as many terminals as conductors.
 
Per NEC 300.20(B), if the junction box shown is ferrous, you'd need to cut a slot between the entry holes of the individual conductors, or otherwise mitigate the potential for inductive heating of the ferrous box. [IIRC, the Canadian Electrical Code only requires this for conductors carrying 200A or more, as the 60 Hz inductive heating for a 15A or 20A branch circuit will be small.]

Cheers, Wayne
 
All knob and tube wiring I saw always had an issue with the insulation falling off. Years ago, I was had a long metal pipe which touched the hot and neutral which ran on opposite sides of a basement. ZAP!
 
Nitpicker
Not like I said it needed air sealed boxes or anything...
N1102.4.6 (R402.4.6) Electrical and Communication Outlet Boxes (Air-Sealed Boxes)

Electrical and communication outlet boxes installed in the building thermal envelope shall be sealed to limit air leakage between conditioned and unconditioned spaces. Electrical and communication outlet boxes shall be tested in accordance with NEMA OS 4, Requirements for Air-Sealed Boxes for Electrical and Communication Applications, and shall have an air leakage rate of not greater than 2.0 cubic feet per minute (0.944 L/s) at a pressure differential of 1.57 psf (75 Pa). Electrical and communication outlet boxes shall be marked "NEMA OS 4" or "OS 4" in accordance with NEMA OS 4. Electrical and communication outlet boxes shall be installed per the manufacturer's instructions and with any supplied components required to achieve compliance with NEMA OS 4.
 