This is from Ontario Building Code (NBC is similar):
3.2.1.2. Storage Garage Considered as a Separate Building
(1) A basement used primarily as a storage garage is permitted to be considered as a separate building for the purposes
of Subsection 3.2.2. and Sentences 3.2.5.13.(2) and (3), provided the floor and roof assemblies above the basement and,
except as permitted by Sentence (2), the exterior walls of the basement above the adjoining ground level are constructed
as fire separations of,
....
------------------------------------------------------------------------
I've seen architectural design following this path:
1. Determine if there is a need to considered a basement storage garage as a separate building;
2. If yes, calculate the floor area and number of floors of the storage garage;
3. Use the number of floors as number of storey (a defined term in OBC), and area to match whatever from "3.2.2.75. Group F, Division 3, up to 6 Storeys, Sprinklered" to "3.2.2.82. Group F, Division 3, 1 Storey, Any Area, Low Fire Load Occupancy", and apply the requirements for design for the purpose of Subsection 3.2.2.
My question: since the storage garage in question is basement, and basement floor number is not qualified to count for building height ( building height means the number of storeys contained between the roof and the floor of the first storey), so, how to determine building height in order to use Article 3.2.2.75 to 3.2.2.82?
3.2.1.2. Storage Garage Considered as a Separate Building
(1) A basement used primarily as a storage garage is permitted to be considered as a separate building for the purposes
of Subsection 3.2.2. and Sentences 3.2.5.13.(2) and (3), provided the floor and roof assemblies above the basement and,
except as permitted by Sentence (2), the exterior walls of the basement above the adjoining ground level are constructed
as fire separations of,
....
------------------------------------------------------------------------
I've seen architectural design following this path:
1. Determine if there is a need to considered a basement storage garage as a separate building;
2. If yes, calculate the floor area and number of floors of the storage garage;
3. Use the number of floors as number of storey (a defined term in OBC), and area to match whatever from "3.2.2.75. Group F, Division 3, up to 6 Storeys, Sprinklered" to "3.2.2.82. Group F, Division 3, 1 Storey, Any Area, Low Fire Load Occupancy", and apply the requirements for design for the purpose of Subsection 3.2.2.
My question: since the storage garage in question is basement, and basement floor number is not qualified to count for building height ( building height means the number of storeys contained between the roof and the floor of the first storey), so, how to determine building height in order to use Article 3.2.2.75 to 3.2.2.82?