Hydrogen detection in a room with UPS systems?

HVACQuestions

REGISTERED
Joined
Sep 23, 2019
Messages
23
Location
02210
In IFC, I'm trying to understand whether or not I need a hydrogen detection system in a room with a UPS. By reading the IFC code, any "battery room" requires H2 detection if constant exhaust is not applied to the room. However doesn't this depend on the size of the battery or UPS inside the room? It makes no sense to install a H2 detection system for only a single 20kW UPS.
 
SECTION 608

STATIONARY STORAGE BATTERY SYSTEMS

608.1 Scope.
Stationary storage battery systems having an

electrolyte capacity of more than 50 gallons (189 L) for

flooded lead-acid, nickel cadmium (Ni-Cd) and valve-regulated

lead-acid (VRLA),
or more than 1,000 pounds (454 kg)

for lithium-ion and lithium metal polymer, used for facility

standby power, emergency power or uninterruptible power

supplies shall comply with this section and Table 608.1.
 