• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

I-2 smoke barrier door construction

From 2009 ibc

Does this apply to section 407.3?

407.3.1 Corridor doors. Corridor doors, other than those in a wall required to be rated by Section 508.2.5 or for the enclosure of a vertical opening or an exit, shall not have a required fire protection rating and shall not be required to be equipped with self-closing or automatic-closing devices, but shall provide an effective barrier to limit the transfer of smoke and shall be equipped with positive latching. Roller latches are not permitted. Other doors shall conform to Section 715.4.

And this section:::

711.5.2 Smoke and draft control doors. Where required elsewhere in the code, doors in smoke partitions shall meet the requirements for a smoke and draft control door assembly tested in accordance with UL 1784. The air leakage rate of the door assembly shall not exceed 3.0 cubic feet per minute per square foot (0.015424 m3/(s ∙ m2)) of door opening at 0.10 inch (24.9 Pa) of water for both the ambient temperature test and the elevated temperature exposure test. Installation of smoke doors shall be in accordance with NFPA 105.

Only doors in smoke partitions that are required elsewhere in the code to be smoke and draft control doors must comply with section. Section 407.3.1 requires corridor doors in Group I-2 to "limit the transfer of smoke"; therefore, those doors must meet this section. Section 708.14.1, Exception 5, requires smoke and draft control doors for the smoke partition exception to elevator lobby enclosures (see commentary, Section 715.4.3.1).
 
Top