I should trust you?
They should have made a new label......
ry%3D400
The solar contractor requested inspection for last Friday. The contractor called that morning and asked the office manager to replace me with another inspector. The reason given was that I and the H/O had a big argument and the H/O doesn't want me on the property. Well that's BS and didn't happen so the office manager said no.
Then the contractor asked to speak to me. He wanted to know what time would I be there. I gave him a two hour window and asked what was done about replacing the service panel. He told me that he had a letter from GE attesting to the fact that the panel is rated at 125 amps and therefor it does not need to be replaced.
Hearing that, I called GE for the second time. I was assured that this panel is rated at 100 amps. I was on hold for five minutes while the GE person searched archive files to find a model number that was retired years ago and there it was...100 amps.
So I get to the job-site and the guy that met me hands me these pictures.
https://flic.kr/p/nAscYi [/URL]
https://www.flickr.com/people/97859466@N05/
My first thought was that whoever did this is better than Dennis.
The story about a letter from GE turned out to be another lie.
chris kennedy said:
Where does that say 125A?
Oh crap, I posted the wrong picture. There I fixed it.
The label looks like it was born yesterday. I really do wonder what's going on.
That would not be hard to do-- I could have done better but I didn't want to spend the time--Also the orange mark thru hides some sins
Now the rest of the story:
I called GE at the first inspection and was assured that the bus rating is 100 amp. I called GE at the second inspection and was assured that the bus rating is 100 amp. Today was the third inspection. The contractor told me that he talked to GE and was told that if a particular 125 amp breaker is installed, the bus rating becomes 125 amp. I called GE before I left the office and was assured that the bus rating is 100 amp.
When I arrived I found that a 125 amp main has been installed. I called GE with the contractor and owner present. We were assured that the bus rating is 100 amp. Then the owner says, "But you told me that the bus becomes 125 amp with xyz breaker" That's when the GE engineer says, "Well there is a footnote in the catalog that this panel-board can have an optional 125 amp main."
It took two weeks and four calls to get the truth. The problem is now that the bus is 125 amp, they still can't use the 120% rule with a 125 amp main. They will put back the 100 amp main.
I still don't trust them. Well we have a history.
Those who ignore history are doomed to repeat it.
Maybe someday this contractor will learn from your history with him...