I have attached a diagram and am curious as to the required width of Corridor A and Corridor B. My reading of 1028.3 Exception is that they would need to dispersed and accommodate 100 percent of the required width. Both Sections 1028.2 and 1028.3 discuss distribution of exits but not really how to get there. Section 1018.2 would require Corridor A and B to be sized according the spaces they serve, but what is that determination?
Is it accommodating all 406 occupants?
Is it to accommodate 300 occupants from the two spaces it serves directly?
Is it to accommodate the 300 occupants plus half of the 106 from the third space (takes into account a fire could disable egress to one of the exits from that space)?
Is it accommodating all 406 occupants?
Is it to accommodate 300 occupants from the two spaces it serves directly?
Is it to accommodate the 300 occupants plus half of the 106 from the third space (takes into account a fire could disable egress to one of the exits from that space)?