• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

IBC 2009 changes affecting fire suppression systems

Re: IBC 2009 changes affecting fire suppression systems

Was the requirement for heat and smoke venting removed in a sprinklered F1 , S1 building? If so, can someone provide a link to this?
 
Re: IBC 2009 changes affecting fire suppression systems

Insurance Engineer

per chap 23 IFC not required if esfr's are used/ section not changed from 06
 
Re: IBC 2009 changes affecting fire suppression systems

Thanks I saw a lot of proposals from removing the requirement to going with FD operated exhaust fans only. I then checked the 2009 IBC and saw it was still in as in the 2006 version. Anyone know what happen and why none of the proposals were accepted?? Requiring Heat & Smoke vents seems to go against a lot of testing done as well as what NFPA 13 and FM says about smoke vents in a building with a sprinkler system, basicly no advantage and perhaps not a good thing at all.
 