Specifically, I'm having a bit of trouble understanding 721.2.1.4.
I need to increase the fire-resistance rating of a existing 5" thick pre-cast concrete panel construction from 2 HR to 3 HR. This is making the presumption that the worst case concrete (siliceous) of that thickness is worth 2 HR per Table 721.2.1.1.
Going to 721.2.1.4, it looks like I have three choices if I want to increase the panel rating by adding layers of 5/8" Type X GWB.
721.2.1.4.1-Nonfire-exposed side
721.2.1.4.2 Fire-exposed side
721.2.1.4.3 Nonsymmetrical assemblies
From a practicality standpoint, we would like to add layers of GWB to one side only (Nonsymmetrical assembly). I've read the commentary but I'm still not sure how to apply 721.2.1.4.1 and 721.2.1.4.2 as required by 721.2.1.4.3.
I would be very grateful if someone could explain this to me.