I have a mixed use project in which the owner wants a single unisex restroom. The occupant loads are as follows:
Business = 11 Occupants
Mercantile = 17 Occupants
Total Occupant Load = 28
Per 2902.2, Exception 4, a Business occupancy can forego having separate facilities if the occupant load is 25 or less.
Per 2902.2, Exception 3, a Mercantile occupancy can forego having separate facilities if the occupant load is 100 or less.
What I BELIEVE needs to happen: Take total occupant load and apply the most stringent requirement of the two occupancies. In this case, the business requirement is the most stringent. We have 28 occupants total. This is greater than 25, therefore we're required to have 2 bathroom facilities.
What I'm questioning: Considering the B occupancy on its own meets 2902.2, Exception 4, AND the Mercantile occupant load meets the requirements of 2902.2, Exception 3, each occupancy on its own is allowed a single unisex restroom. Because of this, I can theoretically provide a single restroom and meet the requirements of both occupancies.
Thank you for any interpretations you can provide.
Business = 11 Occupants
Mercantile = 17 Occupants
Total Occupant Load = 28
Per 2902.2, Exception 4, a Business occupancy can forego having separate facilities if the occupant load is 25 or less.
Per 2902.2, Exception 3, a Mercantile occupancy can forego having separate facilities if the occupant load is 100 or less.
What I BELIEVE needs to happen: Take total occupant load and apply the most stringent requirement of the two occupancies. In this case, the business requirement is the most stringent. We have 28 occupants total. This is greater than 25, therefore we're required to have 2 bathroom facilities.
What I'm questioning: Considering the B occupancy on its own meets 2902.2, Exception 4, AND the Mercantile occupant load meets the requirements of 2902.2, Exception 3, each occupancy on its own is allowed a single unisex restroom. Because of this, I can theoretically provide a single restroom and meet the requirements of both occupancies.
Thank you for any interpretations you can provide.