Hello,
I am looking at the separation between a I-B sprinklered, high-rise 26 feet away from a I-B, S-2 non-sprinklered public parking garage.
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
Table 602 10 ≤ X < 30 IB, S-2 has 1 hour rating with footnote c.
c. Open parking garages complying with Section 406 shall not be required to have a fire-resistance rating.
Confirmed compliance with 406.
Then for the building, if i have 16 feet to the imaginary lot line with B Occupancy the table has 1 with footnote c. However, the table also has footnote g.
g Where Table 705.8 permits nonbearing exterior walls with unlimited area of unprotected openings, the required fire-resistance rating for the exterior walls is 0 hours.
Table 705.8 - MAXIMUM AREA OF EXTERIOR WALL OPENINGS BASED ON FIRE SEPARATION DISTANCE AND DEGREE OF OPENING PROTECTION
705.8 15 to less than 20f, g, j - Unprotected, Sprinklered (UP, S)i - 75% Allowable Area
So does this mean that 25% of the solid exterior wall needs to be 1 hour rated but 75% of glazed openings are not required to be rated? I don't have a commentary for IBC 2018, maybe looking back to 2015 or 2012 commentary would help?
I am looking at the separation between a I-B sprinklered, high-rise 26 feet away from a I-B, S-2 non-sprinklered public parking garage.
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
- The closest interior lot line.
- To the centerline of a street, an alley or public way.
- To an imaginary line between two buildings on the lot.
Table 602 10 ≤ X < 30 IB, S-2 has 1 hour rating with footnote c.
c. Open parking garages complying with Section 406 shall not be required to have a fire-resistance rating.
Confirmed compliance with 406.
Then for the building, if i have 16 feet to the imaginary lot line with B Occupancy the table has 1 with footnote c. However, the table also has footnote g.
g Where Table 705.8 permits nonbearing exterior walls with unlimited area of unprotected openings, the required fire-resistance rating for the exterior walls is 0 hours.
Table 705.8 - MAXIMUM AREA OF EXTERIOR WALL OPENINGS BASED ON FIRE SEPARATION DISTANCE AND DEGREE OF OPENING PROTECTION
705.8 15 to less than 20f, g, j - Unprotected, Sprinklered (UP, S)i - 75% Allowable Area
So does this mean that 25% of the solid exterior wall needs to be 1 hour rated but 75% of glazed openings are not required to be rated? I don't have a commentary for IBC 2018, maybe looking back to 2015 or 2012 commentary would help?