jar546
CBO
This is what the FBC has in this section. Do you think this is better or worse than the IBC?
[F]903.3.1.2.1Balconies and decks.
Sprinkler protection shall be provided for exterior balconies, decks and ground floor patios of dwelling units and sleeping units where the building is of Type V construction, provided there is a roof or deck above. Sidewall sprinklers that are used to protect such areas shall be permitted to be located such that their deflectors are within 1 inch (25 mm) to 6 inches (152 mm) below the structural members and a maximum distance of 14 inches (356 mm) below the deck of the exterior balconies and decks that are constructed of open wood joist construction.[F]903.3.1.2.2Corridors and balconies in the means of egress.
Sprinkler protection shall be provided in corridors and for balconies in the means of egress where any of the following conditions apply:- 1.Corridors with combustible floor or walls.
- 2.Corridors with an interior change of direction exceeding 45 degrees (0.79 rad).
- 3.Corridors that are less than 50 percent open to the outside atmosphere at the ends.
- 4.Open-ended corridors and associated exterior stairways and ramps as specified in Section 1027.6, Exception 3.
- 5.Egress balconies not complying with Sections 1021.2 and 1021.3