According to art. 903.2.1.5:
"Group A-5. An automatic sprinkler system shall be provided for all enclosed Group A-5 accessory use areas in excess of 1,000 square feet (93 m2)."
Does this refer to the aggregate area, or standalone fire areas of 1,000 square feet?
In an outdoor swimming pool installation I have 900 square feet of storage on ground level some 20 feet away from the pool water surface, and another 500 square feet at 10 feet below that , separated by a concrete slab.
Both areas are accessory use to the A-5 swimming pool, pumps, chlorination, pool maintenance equipment etc.
Access to the lower level is by an external open staircase.
Should I add the two levels and go for sprinklers because of that?
"Group A-5. An automatic sprinkler system shall be provided for all enclosed Group A-5 accessory use areas in excess of 1,000 square feet (93 m2)."
Does this refer to the aggregate area, or standalone fire areas of 1,000 square feet?
In an outdoor swimming pool installation I have 900 square feet of storage on ground level some 20 feet away from the pool water surface, and another 500 square feet at 10 feet below that , separated by a concrete slab.
Both areas are accessory use to the A-5 swimming pool, pumps, chlorination, pool maintenance equipment etc.
Access to the lower level is by an external open staircase.
Should I add the two levels and go for sprinklers because of that?