ICC Clarifies Conditions for Duct Penetrations Through Rated Horizontal Assemblies
A recent code interpretation provides critical guidance on whether exhaust ducts are permitted to penetrate fire-resistance-rated horizontal assemblies in multi-family residential buildings. The clarification applies to the 2018, 2021, and 2024 editions of the International Building Code (IBC) and addresses the routing of bath and clothes dryer exhaust ducts through a one-hour rated floor/ceiling assembly in a two-story, Type VB apartment building.
The key provision is IBC Section 717.6.2, which generally requires that ducts penetrating the ceiling membrane of a fire-resistance-rated floor/ceiling assembly be protected with either a shaft enclosure or a ceiling radiation damper. However, there are specific exceptions to this requirement. Notably, Exception 2 of Item 2 permits such penetrations when the duct originates within the dwelling unit and the penetration is protected with a firestop system in accordance with Section 714.5.1.2.
In the case at hand, the exhaust ducts are routed from the bathroom and laundry area up through an interior wall cavity and penetrate the rated floor assembly at the top plate. Once within the floor truss space (the rated horizontal assembly), the ducts run laterally to terminate at a sidewall. According to the ICC’s interpretation, this configuration is permitted—provided that the penetration is firestopped using a tested and listed system that complies with ASTM E814 or UL 1479, as required by Section 714.5.1.2.
The 2018 International Mechanical Code (IMC) Section 504.2 is also relevant. It prohibits the installation of ceiling radiation dampers in dryer exhaust ducts. This creates a conflict unless Exception 2 of Section 717.6.2 is used, which does not require a damper if the penetration is properly firestopped.
Additionally, there is no requirement in the code to install fire-resistive wrapping around the ducts once they are within the horizontal cavity—as long as the ducts remain within the same dwelling unit and do not pass through another unit. In this interpretation, running the exhaust laterally through the ceiling space to reach an exterior wall is considered an extension within the same unit, even if there is a dwelling above, because the ducts do not enter that upper unit’s occupied space.
Conclusion:
Under Exception 2 of Section 717.6.2, and in compliance with Section 714.5.1.2, the proposed method of routing dryer and bath exhaust ducts through the ceiling membrane of a one-hour rated floor/ceiling assembly is code-compliant. Ceiling radiation dampers are not required in this case, and no additional fire-rated duct wrapping is necessary once inside the ceiling cavity, assuming the ducts remain within the originating dwelling unit.
You did not mention the minimum thickness required for the ductwork. SMACNA permits 30 gauge thickness for 4" round duct construction. Domestic dryer ducts are required to be 28 gauge minimum thickness for residential dryer single exhaust systems.
504.9​
Exhaust ducts for domestic clothes dryers shall conform to the requirements of Sections 504.9.1 through 504.9.6.
504.9.1​
Exhaust ducts shall have a smooth interior finish and shall be constructed of metal not less than 0.016 inch (0.4 mm) in thickness. The exhaust duct size shall be 4 inches (102 mm) nominal in diameter.
For the dryer duct penetrations through top plates, the current UL Certified systems state that the "Depth of chase wall stud cavity to be min 1/2 in. (13 mm) greater than diameter of opening cut in top plates to accommodate the through penetrant" and the systems need at least 1/4" annular space. Those requirements are obviously impossible to meet for a 4" duct unless it is in 2x6" stud wall. For correct firestop system installation, dryer ducts need to be routed through 2x6" stud walls. Two systems are attached for reference.