• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

ICC's perspective on 'work area' and its effect on IEBC compliance.

Mr Softy

Silver Member
Joined
Jul 7, 2011
Messages
162
Location
Our Fair City
in our never-ending quest to get a clear, working definition of the 'work area' and it's relationship to Levels 1,2 & 3 work, we recently had an interesting chat with ICC on said subject.

we recently had a 3-family (traditional 3 decker) under renovation on all 3 floors. architect submitted plans dilineating the Level 2 'work area' at 42% of the building. OK. a field inspection revealed work in excess of what was indicated on the plans.

some of the work was exempt as being 'not initially intended'. OK. IEBC includes that exemption as part of the definition.

However, considering everything else being done, including all new systems, it was our interpretation that the work area now was over 50%. so the fire protecton upgrades of 704.2.2 would apply.

as part of our review of the architect's recalculation of work area (under 50%), we contacted ICC to hear their take on 'work area'.

ICC felt that the reconfigured space could/should be calculated as one figure for Level 2 work, and everything else could be calculated at a different figure as Level 1 work. basically allowing Levels 1 & 2 to coexist on the same project, and parsing off the 'reconfigured space' when determining if the project escalates to the upgrades of Level 2 or Level 3. by this method, and with careful math, no project should ever get to a work area of >50%.

both our department, and the state's Fire Services are having a difficult time with this interpretation. IEBC was adopted because it had provisions for updating fire protection, which we have always had in cases of buildings undergoing extensive renovation.

the main difficulty comes with residential multi-family buildings undergoing substantial, building-wide renovation. there is state law governing FP upgrades in commercial buildings. upgrades in residential have always been required through the building code. it has been part of our state's building code intent for many years.

as i see it, IEBC, creatively applied, would/should never require FP upgrades, even though those triggers are part of the code.

the RDP could -

1. pull a permit for limited work, and once underway, call everything else 'not initially intended'. or.

2. calculate work area sq footage to the barest minimum (thickness of wall or door), and never exceed 50% of the floor or total area of the building.

curiouser and curiouser.
 
Stick to your guns, it sound like a gut remodel carefully presented to be below the threshold of requiring all the upgrades. I would make them comply with the upgrades by letter citing chapter and verse and had them the appeal paper work at the same time.

The ICC jus has opinions and is not the enforcing AHJ
 
It is not just 50% of the work area. There are 4 conditions that have to be met before sprinklers are required

704.2.2 Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2.

In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:

1. The work area is required to be provided with automatic sprinkler protection in accordance with the International Building Code as applicable to new construction;

2. The work area exceeds 50 percent of the floor area; and

3. The building has sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump.

Are there corridors shared by different tenants?

Does the building have sufficient water available at the floor?
 
mtlogcabin said:
Are there corridors shared by different tenants?

Does the building have sufficient water available at the floor?
yes, triple decker, shared front stair and back stair.

yes, we're in the city
 
Well, it's deja vu all over again, with an ICC interpretation on top.

You got the code you wanted, now enforce it the way it was written.

Until you can change it to something more danceable.
 
brudgers, i have you on perma-ignore.

i do not know what you posted, nor do i care.

thank you for playing. good bye.
 
I agree the the ICC on this one

Chapter 7 Alterations—Level 2. Like Chapter 6, the purpose of this chapter is to provide detailed requirements and provisions to identify the required improvements in the existing building elements, building spaces and building structural system. This chapter is distinguished from Chapters 6 and 8 by involving space reconfiguration that could be up to and including 50 percent of the area of the building. In contrast, Level 1 alterations (Chapter 6) do not involve space reconfiguration and Level 3 alterations (Chapter 8) involve extensive space reconfiguration that exceeds 50 percent of the building area. Depending on the nature of alteration work, its location within the building and whether it encompasses one or more tenants, improvements and upgrades could be required for the open floor penetrations, sprinkler system or the installation of additional means of egress such as stairs or fire escapes.

Only the reconfigured space/areas count towards level 2 or 3 and without knowing the specific details of the project it is hard say if it exceeds 50% or not. The designer does have the option of using 101.5.3 Performance compliance method and it could be 100% reconfiguration and not require sprinklers.

[h=2]re·con·fig·ure[/h]   /ˌrikənˈfɪgyər/ Show Spelled[ree-kuhn-fig-yer] Show IPA

verb (used with object), re·con·fig·ured, re·con·fig·ur·ing. to change the shape or formation of; remodel; restructure.
 
Softy...if the project scope does not match the permit scope, then re-review the project for the actual scope in accordance with your adopted codes. If the codes do not meet the expectations of the AHJ, whether it is due to loop holes or vague language, then you may go down the amendment and policy change road for future projects, I recommend not changing the rules mid-game if your expectations are not being met now, even if the owner/RDP are trying to pull a fast-one over on you.

It might be time to put on your waffle cone pants. Good luck.
 
brudgers said:
Well, it's deja vu all over again, with an ICC interpretation on top. You got the code you wanted, now enforce it the way it was written.

Until you can change it to something more danceable.
brudgers said:
I'm in good company. You ignore the building code too.
With a Milton's rule sig, that is very small of you brudgers.

The least you could do is put on your plans examiner hat one more time and give us a step by step account of how the brudger's would have approved this set of plans.

Softy...maybe a few more details in line with mt's posts would be helpful too.
 
Papio Bldg Dept said:
With a Milton's rule sig, that is very small of you brudgers. The least you could do is put on your plans examiner hat one more time and give us a step by step account of how the brudger's would have approved this set of plans. Softy...maybe a few more details in line with mt's posts would be helpful too.
I think you misunderstand Milton's Rule. It doesn't mean that every set of plans get approved.

Or that one ignores the code.

What Milton's Rule means is that one approaches plan review with the hope of approving the plans and feels disappointment rather than satisfaction when one cannot.

What Milton's Rule means is that if placing a simple notation on the plans is the difference between approving and rejecting the plans, you place the notation.

What Milton's Rule means is that if a phone call to the design professional can get you what you need to approve the plans in a day or two, then you make the call.

But above all, what Milton's Rule means is that you don't go searching for reasons to reject the plans, you don't go stretching your interpretation in order to reject the plans, and you don't bring a chip on your shoulder, a righteous agenda, or any other prejudice to your review...

In practice that requires interpreting the code in light of common practices.

In practice that requires interpreting the code to let people go about their business in a reasonably safe manner.

Most importantly, in practice it requires allowing things that you don't really like.

...or at least that's what you try to do.

That's not the case here. Unsurprisingly.
 
mtlogcabin said:
Only the reconfigured space/areas count towards level 2 or 3 and without knowing the specific details of the project it is hard say if it exceeds 50% or not. The designer does have the option of using 101.5.3 Performance compliance method and it could be 100% reconfiguration and not require sprinklers.
yes, he does, if the existing building meets the criteria set forth in 101.5.1. agreed.

and here we are with that nebulous phrase 're-configured space' again. one might see a moved wall and see an entire room as having been reconfigured. another might look and see only a wall.

Papio Bldg Dept said:
Softy...if the project scope does not match the permit scope, then re-review the project for the actual scope in accordance with your adopted codes.
which is what happened, and this is when it usually comes up. submitted drawings show one thing, field conditions reveal something completely different. after consideration, it was agreed that the scope was still under 50%, applying ICCs interpretation on Level 1 and Level 2 co-existing.

Papio Bldg Dept said:
If the codes do not meet the expectations of the AHJ, whether it is due to loop holes or vague language, then you may go down the amendment and policy change road for future projects ...
this is the path being followed with the state code board.

Papio Bldg Dept said:
I recommend not changing the rules mid-game if your expectations are not being met now, even if the owner/RDP are trying to pull a fast-one over on you.
agreed.

here's the crux of the biscuit, so to speak.

why does the IEBC have any language at all regarding FP upgrades as triggered by scope of work, when, by their own definitions and interpretations, one can use creative accounting and NEVER get there?

in the examination of the IEBC before adoption, the work area method of requiring FP upgrades looked pretty good. we have always had a trigger for these upgrades in our homegrown code - as i stated it's been a core philosphy of our building code for many years. the upgrades were based on cost of work compared to cost of sprinklers. but it was pretty easy to game that system and avoid sprinkling buildings undergoing 'substantial renovation' (our code term).

as we're now into a year+ of the IEBC, the flaws in the system, and the difficulty of consistent enforcement are coming to light.

and as stated above, this is a residential renovation issue.

so.

can someone give me an example, hypothetical or real, of Level 2 or Level 3 residential work in which the 50% rule would kick in?
 
Mr Softy said:
as we're now into a year+ of the IEBC, the flaws in the system, and the difficulty of consistent enforcement are coming to light.
Well, the way to be consistent is to enforce the code as written.
 
brudgers said:
Well, the way to be consistent is to enforce the code as written.
Which it appears softy is trying to do that, however we are dealing with near Falstaff-ian greatness here. In brudger terms, it is the code equivalent of asking a guard to stand outside a tower door and make sure nobody leaves.
 
can someone give me an example, hypothetical or real, of Level 2 or Level 3 residential work in which the 50% rule would kick in?
See Section 403

Gutting a kitchen and relocating the plumbing fixtures and cabints or counters. Expanding a laundry room or bathroom. Removing or adding walls.

Replacing a door or windows would not include the entire floor space in the affected room. These items are under level 2 because when replaced they are required to meet todays code. Doors for egress size, swing and hardware, Windows for EERO, safety glazing, energy code to name a few.

The IEBC is similar to Pelosie's comment on Obama care.

"We have to adopt it to find out what's in it"

Until we start using a code regularly and consistantly we really do not have an understanding of what's in it.

I have a bigger problem with this part than figuring work areas

. The building has sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump.

Does that mean a riser already has to be inplace or just that the municiple water supply will be able to provide water to the height needed without a fire pump. The latter seems logical but the actual wording indicates the water supply needs to exist within the building.

From a literal interpretation I do not see where a spinkler can be required in a building that does not have a riser stand pipe already installed

What are your thoughts?
 
mtlogcabin said:
See Section 403Gutting a kitchen and relocating the plumbing fixtures and cabints or counters. Expanding a laundry room or bathroom. Removing or adding walls.
is this the 50% example? or just examples of Level 2? the first sentence is Level 1 - no reconfiguration - unless the cabinet layout is different, then maybe... :)

Replacing a door or windows would not include the entire floor space in the affected room. These items are under level 2 because when replaced they are required to meet todays code. Doors for egress size, swing and hardware, Windows for EERO, safety glazing, energy code to name a few.
no, they are not Level 2, unless they are relocated windows or doors. if they are straight replacements in the existing opening, that is level 1. and yes, they need to meet code for new const.

Until we start using a code regularly and consistantly we really do not have an understanding of what's in it.
yup.

I have a bigger problem with this part than figuring work areas

. The building has sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump.

Does that mean a riser already has to be inplace or just that the municiple water supply will be able to provide water to the height needed without a fire pump. The latter seems logical but the actual wording indicates the water supply needs to exist within the building.

From a literal interpretation I do not see where a spinkler can be required in a building that does not have a riser stand pipe already installed

What are your thoughts?
this.
 
Papio Bldg Dept said:
Which it appears softy is trying to do that, however we are dealing with near Falstaff-ian greatness here. In brudger terms, it is the code equivalent of asking a guard to stand outside a tower door and make sure nobody leaves.
I'm reminded more of the progress of Lancelot running toward the guards at the gate.
 
Mr Softy said:
why does the IEBC have any language at all regarding FP upgrades as triggered by scope of work, when, by their own definitions and interpretations, one can use creative accounting and NEVER get there?
Sometimes, I just say I don't know the answer...this one of those sometimes.

Mr Softy said:
can someone give me an example, hypothetical or real, of Level 2 or Level 3 residential work in which the 50% rule would kick in?
Yes, the one in which the RDP designs it that way.
 
Good example.

It's a change of occupancy as defined in Section 2. But the occupancy classification doesn't change (so 912 doesn't apply)

But Chap 4 kicks in. And here we go with 'work area' again.

In your example, are you going to consider the total square footage of the newly created units as the 'reconfigured space'?

Because I'm going to use ICC interp and only count the area of the moved walls and new doors as level 2 work and stay well under the 50% triggers.

But wait. The reconfiguration of the heating system counts as Level 2 work. But I'll only count the new mechanical closet as reconfigured. And I'll still be under 50% triggers.
 