Sifu
- Joined
- Sep 3, 2011
- Messages
- 3,465
Question: Is panic hardware required in this existing building, change of occupancy?
2018 IEBC. Previous occupancy M, changed to A2, occupant load 65. No changes proposed to the two exit doors from the space.
IEBC definitions would classify this as a C of O (because it is a change of occupancy classification). IEBC 202.
IEBC 1001 indicates ch. 10 applies, further refined as a partial change of occupancy by 1001.2.2.1, which sends us directly to 1011.
IEBC 1011.1 validates that section 1011 applies to a partial change of occupancy, which compels compliance with 1002 through 1010, as well as 1011.
So now we have it. This project is subject to IEBC 1002 through 1011.
IEBC 1011.4.2 sends us to IEBC 905.
IEBC 905 sends us to IEBC 805. IEBC 805.4.4 tells us that panic is required if the A OL is >100, HOWEVER 805.1 tells us this section is limited to where an exit or corridor is shared by more than 1 tenant.
Wait, now we have it. This is subject to ch. 10, ch. 9, and ch. 8, sometimes.
Note that the IEBC general comments tells us not to confuse a change of occupancy with a change of occupancy classification but defines a change of occupancy as a change of occupancy classification. I get the nuances, but to me this is word salad.
Note that in 2 of the 3 hazard tables, an A2 is a greater hazard than an M, but not the MOE table.
Note that the commentary for 805.4.4 tells us this requirement is "much the same" as IBC 1010.1.10. IMHO it is not "much the same".
Note that IEBC 1011.1 tells us that the application of requirements for the change of occupancy shall be as set forth in 1011.1.1 through 1011.1.4. There is no 1011.1.4. (The '21 and '24 must have figured that out, or accidentally fixed it with renumbering/reconfiguration).
So a single tenant, A2 occupancy, without shared exits with an OL of 99 doesn't require panic hardware, but maybe if not sharing the exits the OL is unlimited and no panic is required.
Sorry, kind of a rant. The IEBC was intended to make existing buildings more usable without full compliance with the IBC. I get it, but is panic hardware one of the deal-breakers? If so, fine. Tell us that without all the contortions. These are challenges I have in understanding the IEBC, and making it a usable resource for DP's, owners and contractors.