CMU should fulfill the requirements of a thermal barrier. Maintaining the 2 hour rating depends. If it is a UL marked cmu (haven't seen one in years) then look at the listing. If it is common cmu then 721.3.2 & Table 721.3.2 should provide some guidance.barlovian said:Is foam insulation permitted in the cores of cmu at exterior walls in Type IIIb construction? Or, is combustible insulation only permitted as part of an interior or exterior finish? (Ref 2006 IBC 602.3, 2603.5)
Yes, it would make things more clear if there were some language in Chapter 6 that gave us the exceptions for type III as it does for types I and II, but 2603.5 if very specific in stating that it covers exterior walls of buildings of type III along with the others. 2603.5 is more specific than Chapter 6 (it deals specifically with foam insulation in exterior walls), so in accordance with the last sentence of 102.1 I think 2603.5 trumps the more general requirements in Chapter 6.barlovian said:I don't see a section similar to 603.1 for Type III construction to provide exceptions to the requirement that IIIb exterior walls be non-combustible.