• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

"in-use covers"

spector51

Registered User
Joined
Oct 22, 2012
Messages
32
Location
DC, Northern VA
In a commercial application, when does the NEC require the use of an "In-use Cover" on an outdoor receptacle. Receptacle is already GFCI protected. Does the code language imply it is only required when needed. I have a rooftop area in an office building that will sometimes be used to host cocktail parties and other marketing events. I can see the receptacles used for crock pots, music, festival lighting, etc.

Thanks
 
Noticed that this section requires extra heavy duty for other than dwelling units where the device is supported from grade as described in 314.23(B). Usually these are die cast or some kind of metal.

WP1250MVXD_depth.ashx
 
Yeah, the cheap residential ones usually barely make it through final inspection.........
 