good question, another one have not thought of. Not sure if it counts?? in away
Guess you could look at fire history in an indoor pool, but that does not take into account max exiting because of a floating babyruth bar.
Look at 1016.1 exception 1 and 2, I know it is not outdoors
Exceptions 1 and 2 provide for a travel distance terminating at the top of an open exit stair in an open parking structure, or an open exit stair or ramp in outdoor facilities (e.g., stadiums, exterior stairways from open balconies, observation decks and amusement structures) (see Section 1022.1, Exceptions 2 and 4). This is appropriate in view of the low hazard in these facilities.
also::
1022.1 Enclosures required. Interior exit stairways and interior exit ramps shall be enclosed with fire barriers constructed in accordance with Section 707 or horizontal assemblies constructed in accordance with Section 712, or both. Exit enclosures shall have a fire-resistance rating of not less than 2 hours where connecting four stories or more and not less than 1 hour where connecting less than four stories. The number of stories connected by the exit enclosure shall include any basements but not any mezzanines. Exit enclosures shall have a fire-resistance rating not less than the floor assembly penetrated, but need not exceed 2 hours. Exit enclosures shall lead directly to the exterior of the building or shall be extended to the exterior of the building with an exit passageway conforming to the requirements of Section 1023, except as permitted in Section 1027.1. An exit enclosure shall not be used for any purpose other than means of egress.
Exceptions:
1. In all occupancies, other than Group H and I occupancies, a stairway is not required to be enclosed when the stairway serves an occupant load of less than 10 and the stairway complies with either Item 1.1 or 1.2. In all cases, the maximum number of connecting open stories shall not exceed two.
1.1. The stairway is open to not more than one story above its level of exit discharge; or
1.2. The stairway is open to not more than one story below its level of exit discharge.
2. Exits in buildings of Group A-5 where all portions of the means of egress are essentially open to the outside need not be enclosed.
3. Stairways serving and contained within a single residential dwelling unit or sleeping unit in Group R-1, R-2 or R-3 occupancies are not